Line-interactive
Line-Interactive UPS. Typical protection time: 5 - 30 minutes. Capacity expansion: Several hours
The Line-Interactive UPS is similar in operation to a Standby UPS, but with the addition of a multi-tap variable-voltage autotransformer. This is a special type of that can add or subtract powered coils of wire, thereby increasing or decreasing the magnetic field and the output voltage of the transformer.
This type of UPS is able to tolerate continuous undervoltage
and overvoltage surges without consuming the limited reserve battery power. It instead compensates by auto-selecting different power taps on the autotransformer. Changing the autotransformer tap can cause a very brief output power disruption, so the UPS may
chirp
for a moment, as it briefly switches to battery before changing the selected power tap.
Autotransformers can be engineered to cover a wide range of varying input voltages, but this also increases the number of taps and the size, weight, complexity, and expense of the UPS. It is common for the autotransformer to only cover a range from about 90v to 140v for 120v power, and then switch to battery if the voltage goes much higher or lower than that range.
In low-voltage conditions the UPS will use more current than normal so it may need a higher current circuit than a normal device. For example to power a 1000 watt device at 120 volts, the UPS will draw 8.32 amps. If a brownout occurs and the voltage drops to 100 volts, the UPS will draw 10 amps to compensate. This also works in reverse, so that in an overvoltage condition, the UPS will need fewer amps of current.
Double-conversion / online
The Online UPS is ideal for environments where electrical isolation is necessary or for equipment that is very sensitive to power fluctuations. Although once previously reserved for very large installations of 10kW or more, advances in technology have permitted it to now be available as a common consumer device, supplying 500 watts or less. The Online UPS is generally more expensive but may be necessary when the power environment is "noisy" such as in industrial settings, for larger equipment loads like data centers, or when operation from an extended-run backup generator is necessary.
The basic technology of the online UPS is the same as in a Standby or Line-Interactive UPS. However it typically costs much more, due to it having a much greater current AC-to-DC battery-charger/rectifier, and with the
and inverter designed to run continuously with improved cooling systems. It is called a
Double-Conversion
UPS due to the rectifier directly driving the inverter, even when powered from normal AC current.
In an Online UPS, the batteries are always connected to the inverter, so that no power transfer switches are necessary. When power loss occurs, the rectifier simply drops out of the circuit and the batteries keep the power steady and unchanged. When power is restored, the rectifier resumes carrying most of the load and begins charging the batteries, though the charging current may be limited to prevent the high-power rectifier from overheating the batteries and boiling off the electrolyte.
The main advantage to the on-line UPS is its ability to provide an electrical firewall between the incoming utility power and sensitive electronic equipment. While the Standby and Line-Interactive UPS merely filters the input utility power, the Double-Conversion UPS provides a layer of insulation from power quality problems. It allows control of output voltage and frequency regardless of input voltage and frequency.
经过纯在线式双转换ups输出的波形和电压是理想状态下的交流电
上文摘自E文版Wikipedia